• IP addresses are NOT logged in this forum so there's no point asking. Please note that this forum is full of homophobes, racists, lunatics, schizophrenics & absolute nut jobs with a smattering of geniuses, Chinese chauvinists, Moderate Muslims and last but not least a couple of "know-it-alls" constantly sprouting their dubious wisdom. If you believe that content generated by unsavory characters might cause you offense PLEASE LEAVE NOW! Sammyboy Admin and Staff are not responsible for your hurt feelings should you choose to read any of the content here.

    The OTHER forum is HERE so please stop asking.

Serious NUH power outage - Old Man Very Angry liao

rambo22

Alfrescian
Loyal
http://www.straitstimes.com/singapore/patients-diverted-as-nuh-hit-by-power-outage

more to cum

cos old man feel no face to have such an dishonorable son

A power outage at the National University Hospital (NUH) yesterday resulted in ambulances being diverted to other hospitals and patients in the affected area directed to other parts of the hospital.

The power went out at 4.15pm for 11/2 hours and affected mainly the first floor of NUH's main building.
 
Last edited:

Cottonmouth

Alfrescian
Loyal
Strangle his fucking dishonourable son of a bitch and strike him with a lightning, what the fuck is he doing switching off lights? He looking for Gecko's corpse to fuck in the dark??? :oIo:
 

halsey02

Alfrescian (Inf)
Asset
http://www.straitstimes.com/singapore/patients-diverted-as-nuh-hit-by-power-outage

more to cum

cos old man feel no face to have such an dishonirable son

A power outage at the National University Hospital (NUH) yesterday resulted in ambulances being diverted to other hospitals and patients in the affected area directed to other parts of the hospital.

The power went out at 4.15pm for 11/2 hours and affected mainly the first floor of NUH's main building.

Ok!...the golden question?, no prize to be given or wanted....Don't these places like hospitals, have BACK UP POWER?, Emergency Generator(s) or preparation for such "EMERGENCY"?? this is peace time...we are not prepared for such power outage in an EMERGENCY department of a hospital....no emergency backup?

The hospital admin & Maintenance must come clean ....no one committed "harakiri"??...it must hen be a honest mistake or act of gourd!:rolleyes:
 

Leongsam

High Order Twit / Low SES subject
Admin
Asset
Ok!...the golden question?, no prize to be given or wanted....Don't these places like hospitals, have BACK UP POWER?, Emergency Generator(s) or preparation for such "EMERGENCY"?? this is peace time...we are not prepared for such power outage in an EMERGENCY department of a hospital....no emergency backup?

The hospital admin & Maintenance must come clean ....no one committed "harakiri"??...it must hen be a honest mistake or act of gourd!:rolleyes:

All hospitals in first world nations have backup generators that keep things going in the event of a power failure.
 

Seee3

Alfrescian (Inf)
Asset
Ok!...the golden question?, no prize to be given or wanted....Don't these places like hospitals, have BACK UP POWER?, Emergency Generator(s) or preparation for such "EMERGENCY"?? this is peace time...we are not prepared for such power outage in an EMERGENCY department of a hospital....no emergency backup?

The hospital admin & Maintenance must come clean ....no one committed "harakiri"??...it must hen be a honest mistake or act of gourd!:rolleyes:

Standby generator will only cut in when the main incoming from Singapore Power failed. From the report, power disruption affected only 1 level so it should probably be internal tripping and the supply from SP should be normal.

For critical places like operating theatre, there should be UPS system to mitigate any localized power disruption.
 

halsey02

Alfrescian (Inf)
Asset
Standby generator will only cut in when the main incoming from Singapore Power failed. From the report, power disruption affected only 1 level so it should probably be internal tripping and the supply from SP should be normal.

For critical places like operating theatre, there should be UPS system to mitigate any localized power disruption.

I know, that is at the Sub-station within the hospital, where the incoming power is distributed to the various power lines & distributed out again through....there is a standby power generator there. But this is the hospital EMERGENCY Department...the word is "emergency"...there should be UPS or UPS system...to kick in on stand by for at least 1 hour....

It means that...it is a honest mistake! :biggrin:
 

tanwahtiu

Alfrescian
Loyal
Olf fart turned into nasty ghost goes round Singapore to damage major installations. Angry at Sinkies cursed at his name everytime people talked bad of Singapore.

Served old fart right for being a nasty bastard who bullied Sinkies for 50 years.
 

Seee3

Alfrescian (Inf)
Asset
I know, that is at the Sub-station within the hospital, where the incoming power is distributed to the various power lines & distributed out again through....there is a standby power generator there. But this is the hospital EMERGENCY Department...the word is "emergency"...there should be UPS or UPS system...to kick in on stand by for at least 1 hour....

It means that...it is a honest mistake! :biggrin:

Just for technical discussion.

UPS and standby generators are only temporary supplies. For critical equipment which will crash even with split second power disruption, UPS is needed as generator will need a few seconds to cut in.

Whether it is UPS or generator, they are not meant to provide normal operation. They are just to buy time to allow a proper shut down of the existing operation or to transfer operation to alternative sites. However, most end users misunderstood that they are to ensure normal operation while power is being restored. Most of the time, power is restored within a short time and that give wrong impression to the purpose of such standby power supplies.

For NUH case, we cannot fault them for diverting ambulances as it is a correct sop as no one can be sure that the UPS supported equipment in their A&E can last till the time that power is restored.
 

johnny333

Alfrescian (Inf)
Asset
This will probably be treated as another honest mistake & the incident swept under the carpet.

However if the gecko or LKY was still alive & at the hospital when this happen, you can be assured that heads would roll.
 

halsey02

Alfrescian (Inf)
Asset
Just for technical discussion.

UPS and standby generators are only temporary supplies. For critical equipment which will crash even with split second power disruption, UPS is needed as generator will need a few seconds to cut in.

Whether it is UPS or generator, they are not meant to provide normal operation. They are just to buy time to allow a proper shut down of the existing operation or to transfer operation to alternative sites. However, most end users misunderstood that they are to ensure normal operation while power is being restored. Most of the time, power is restored within a short time and that give wrong impression to the purpose of such standby power supplies.

For NUH case, we cannot fault them for diverting ambulances as it is a correct sop as no one can be sure that the UPS supported equipment in their A&E can last till the time that power is restored.

Ok, I understand....if NUH is the only hospital, the nearest is 100km...at least they could have some sort of backup...anyway, there is more to meet the eye...I agree with your explanation...that is the proper procedure...
 

tanwahtiu

Alfrescian
Loyal
Under lhl pap contractors and civil serpent jiak liu corrupt like hell.

Even want to najib wang w hospital places 不知死。

Ok, I understand....if NUH is the only hospital, the nearest is 100km...at least they could have some sort of backup...anyway, there is more to meet the eye...I agree with your explanation...that is the proper procedure...
 

eatshitndie

Alfrescian (Inf)
Asset
Just for technical discussion.

UPS and standby generators are only temporary supplies. For critical equipment which will crash even with split second power disruption, UPS is needed as generator will need a few seconds to cut in.

Whether it is UPS or generator, they are not meant to provide normal operation. They are just to buy time to allow a proper shut down of the existing operation or to transfer operation to alternative sites. However, most end users misunderstood that they are to ensure normal operation while power is being restored. Most of the time, power is restored within a short time and that give wrong impression to the purpose of such standby power supplies.

For NUH case, we cannot fault them for diverting ambulances as it is a correct sop as no one can be sure that the UPS supported equipment in their A&E can last till the time that power is restored.

ups relies on battery backup while backup generator, usually diesel powered, requires cranking up and startup time of at least 6.9 minutes. it resupplies electric power to battery banks, not necessarily providing power directly to offices affected. in data center here, we have 16 hours of battery backup and 3+1 diesel generators, meaning 3 active generators running on hot standby with 1 on cold standby. they are connected to the grid and are part of a comprehensive power distribution network 24 by 7 by 365. if disaster or disruption happens, cannot rely on fuel supply to the generators, thus must cut seamlessly over to another site 69 miles away using geographic redundancy. if both sites fail simultaneously like a major earthquake event or nuclear first strike must rely on sites in the rocky mountains buried deep and hardened. sg doesn't have the luxury of true geographic redundancy. when shit hits the fan she is extremely vulnerable. but sinkies will continue to kpkb about little inconveniences.
 
Last edited:

scroobal

Alfrescian
Loyal
The point is no first tier hospital with A&E status should see such a situation. No amount of technical explanation can cover the issue.

Singaporeans are easily fooled by the myriad of technical reasons that follows each and every mishap - from floods to MRT.

I remember one cabinet minister explained hospital bed shortage to school holidays and idiots bought it.

Just for technical discussion.

UPS and standby generators are only temporary supplies. For critical equipment which will crash even with split second power disruption, UPS is needed as generator will need a few seconds to cut in.

Whether it is UPS or generator, they are not meant to provide normal operation. They are just to buy time to allow a proper shut down of the existing operation or to transfer operation to alternative sites. However, most end users misunderstood that they are to ensure normal operation while power is being restored. Most of the time, power is restored within a short time and that give wrong impression to the purpose of such standby power supplies.

For NUH case, we cannot fault them for diverting ambulances as it is a correct sop as no one can be sure that the UPS supported equipment in their A&E can last till the time that power is restored.
 
Last edited:

blackmore

Alfrescian
Loyal
Its a omen of signs of things to come on Honeymah nomination day. Even the doctors say it never happened like that for 20 years he was in NUH.
 

virus

Alfrescian
Loyal
Just for technical discussion.

UPS and standby generators are only temporary supplies. For critical equipment which will crash even with split second power disruption, UPS is needed as generator will need a few seconds to cut in.

Whether it is UPS or generator, they are not meant to provide normal operation. d.

Ups is farked, should use honest bee, ninja or dhl
 

Seee3

Alfrescian (Inf)
Asset
The point is no first tier hospital with A&E status should see such a situation. No amount of technical explanation can cover the issue.

Singaporeans are easily fooled by the myriad of technical reasons that follows each and every mishap - from floods to MRT.

I remember one cabinet minister explained hospital bed shortage to school holidays and idiots bought it.
If the supporting services are backup by standby generator with huge fuel supply tank, then ambulances need not be diverted so quickly. There will be more time for the technician to make an assessment. Therefore, the issue is in the design which would have affected the construction cost. Probably, having a fully backup A&E for NUH was not considered necessary at that time as it is not the main hospital. If sgh is the same, then we really need to relook at our installations.

Mrt's problem is different. Probably more a case of negligent and ignorant. A dear price we are paying for having incompetent people in charge till now. A few breakdown may be due to sabotage. To operate a service that has only very little time for maintenance, the crew must be competent. Such knowledge comes only from experience and exposure to the very system itself, not from books. Even if we bring in the top crew from say Japan, they will need some time to understand and identify all the problem. They can still do it because their attitude is different. Here, we put a bunch of people who are only more interested in finding excuses for failures will never fit it again. All they know is get a consultant or replace and upgrade.
 
Last edited:

halsey02

Alfrescian (Inf)
Asset
If the supporting services are backup by standby generator with huge fuel supply tank, then ambulances need not be diverted so quickly. There will be more time for the technician to make an assessment. Therefore, the issue is in the design which would have affected the construction cost. Probably, having a fully backup A&E for NUH was not considered necessary at that time as it is not the main hospital. If sgh is the same, then we really need to relook at our installations.

Mrt's problem is different. Probably more a case of negligent and ignorant. A dear price we are paying for having incompetent people in charge till now. A few breakdown may be due to sabotage. To operate a service that has only very little time for maintenance, the crew must be competent. Such knowledge comes only from experience and exposure to the very system itself, not from books. Even if we bring in the top crew from say Japan, they will need some time to understand and identify all the problem. They can still do it because their attitude is different. Here, we put a bunch of people who are only more interested in finding excuses for failures will never fit it again. All they know is get a consultant or replace and upgrade.

All it takes is one of the "elite" to get caught in that situation of ever to go emergency department & there is a major power failure there, then, they will sit up & do something. Then again, it is HSK or....the emergency unit will come to them...

My point is, we all know the SOP the technicality of backups etc...for many of us have worked in critical areas where power backups is essential like data centers etc... but, the point is....how prepared are we in National Emergencies?...in critical areas like EMERGENCY DEPARTMENTS of hospitals....what is there was a major accident within 2 KM from NUH & the quicker to the hospital saves lives.....there is a power failure at the ER Dept NUH....how many lives, you think will be "saved"??

Like one of their 'holey' mantra chanting wisecracks says...."any one came clean?, anyone committed harakiri or the head or ER resigned?"